You're right that the green coils prior to VPI deprive you of an opportunity to perform 100% testing of hi-pot and surge testing on every coil.
With global VPI, a very good option is to request that a few coils be set aside and placed in a pair of "mock" slot which have similar dimensions to machine slots. Then the mock coils/slots are subject to the VPI process along with the stator. Then the mock coils are subject to surge and/or dc hi-pot test until failure. Hopefully failure occurs above established minimums (2*KV+1). Either way you can try to identify the point of failure (possibly apply a current and look for smoke at the point of the short). Then section the coil and look for voids.
If you can't produce a failure, you should secton the center of the slot (axially) on the mock coil since impregnation is poorest there, as well as the bends in the end-turn area where the tape insulation tends to bunch and create voids.
I think a full ac or dc hi-pot at the factory is almost a necessity. If you don't do that, then you're limited in your ability to do subsequent field hi-pot testing even at reduced voltage. And the reliability of the machine will forever be questionable.
If you're concerned about the schedule impacts of a hi-pot failure, then stick with the dc hi-pot for two reasons:
#1 - less collateral damage in the event of test failure since the current trip setting is very low (in contrast ac hi-pot current trip must be set high to supply capacitive current.
#2 - You can use a "step-voltage" method on the dc test where you increase voltage in perhaps 15 uniform steps. Hold one minute at each step and record leakage current. Plot current vs voltage. A trend in current vs voltage which increases more than linearly is an early indication of problems (usually end-turn contamination). At that poinot you should stop the test and decide what action to take (no damage has been done if you don't go the point of test set trip). Even with this method, some slot failures do not give much warning. End turn leakage failures give more warning.