BronYrAur
Mechanical
- Nov 2, 2005
- 799
Just need to confirm my thinking. When using a cooling coil to dehumidify, you are limited by the temperature of the coil, correct? In other words, if I have a 55 deg F coil, the best I can do it achieve 55 deg dewpoint, which gives a HR around 65 Gr/lb. Reheating the air is a horizontal line to the right on the psyc chart, which does nothing for absolute humidity (only relative). So, if I have a 70 deg discharge air temp, I am sitting at around 60% RH. If I need 70 deg and 50% RH, I either need to lower my coil temp or introduce a desiccant, etc. Agree? It will not help me to run the unit longer or try to push more air through it, right? No matter how much air I move and no matter how much coil "contact time" I have, I can never do better than the dewpoint temp of the coil. Please share your thoughts.