Control valve sizing.

Status
Not open for further replies.

Indy

Industrial
Dec 14, 2012
172
Hi,
With regards to control valve sizing can anyone point me in the direction of the standard/steps that are required to properly size a control valve.

Thanks
 
Replies continue below

Recommended for you

Thanks for the reply. I will download it.
 
General rules of thumb for pneumatically controlled valves:
1) Try to make all flow scenarios fit between 20% open percentage and 80% open percentage
2) dP at design point should be 10 psi or 10% system pressure, greater of the two
3) Typically the valve will end up being one line size smaller (ie, 4" valve in a 6" line)


That's the absolute basics and then you get quotes/manufacturer data and figure out which valve will work best.
 