Hi, guys.
Any control valve as indicated by JLSEAGULL is throttling purpose, and control valve shall be design following ASME 16.34, 31.3, ISA 75, IEC 60534, FCI 70-2, these are the main standard that every oil and gas company in the world follow to design control valves.
The 1.5 factor that you are talking about, maybe is related to trim selection, due there are three main trim types (plus modifications to these ones): Quick Opening, Equal Percentage and Lineal, the difference among then is because a) Lineal trim produce an similar flow performance since the plug start opening, b) EQ% shape have a smooth performance, so this one is the first choice, due loop tuning at DCS are more accurate and easy to set.
Depending on trim type, the influence on the CV is affected.
So, some oil companies are ruled for the following:
The sizing Cv for equal percentage characteristic valves (specified in data sheets) shall be based on 1.8 times the normal flow calculated Cv or 1.2 times the maximum flow calculated Cv, whichever is the greatest.
- The sizing Cv for linear characteristic valves shall be based on 1.5 times the normal flow calculated Cv or 1.1 times the maximum flow calculated Cv, whichever is greater.
But returning to Shutoff pressure, we usually select the actuator based on the minimum actuator capable to handle the high inlet pressure that the control would received.
These factor helps the instrument guy in the follow
1.- Avoid vendor to sell you a actuator that is oversized (cost, civil, pds, pipping issues)
2.- Control Valves vendor have usually actuator size standard, but if required, the can produce an different one, not recommended!
3.- The actuator function is to Close or Open the control valve, if the vendor confirm that the actuator is suitable to handle the higher inlet pressure, ok, you have to find a actuator that match that pressure value or even better is higher that than.
I hope this help you.