Beware of the 300m cable length, it means 300m of CABLE and not 300m between the unit and the rack room.
This is a typical requirement for field instrumentation and the ONLY one that can waive that requirement is the OEM, preferably: in writing.
Can this requirement be waived?
Well... it all depends on the application, if it is a thermocouple... almost certainly not, you are dealing with millivolts.
If it is a 4-20mA signal, maybe... provided that proper shielding and segregation from other voltage levels is approved by the OEM.
If it is a digital signal, 24VDC and above, probably yes.
saludos.
a.