Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Control Air Damper selection

123131415

Mechanical
Joined
Nov 13, 2006
Messages
20
Location
IN
This Post is regarding selection of control damper .

Duct pressure classification given as 2 inch w.g..

Usually control damper rated for the maximum pressure and maximum velocity, beyond which damper may not performed the indented purpose and hence the operating condition shall not exceed these limits. Duct pressure class is based on the maximum operating range i.e 1,2 ,3 inch W.G etc.

I need clarification on following

1. How much maximum operating pressure of the damper should be greater than duct pressure class.

2.maximum velocity will be occurs at discharge of the fan and hence we can consider the same velocity to compare face velocity.

3. Some manufacture rate the damper for temperature Range application. is there is any requirement from SMACNA or AMCA for air damper which being used in HVAC system

kindly provide some reference material/industry recommended practice used in HVAC .

Thank you
 

Part and Inventory Search

Sponsor

Back
Top