While it is an “old style” it is used in the north Qld a lot, home of 300 days of sunshine a year, it is currently frezzing in my office and i would love to go back right now.
but onto subject;
Your question is a touch open, i have done a few of these building and wall length and slab span are your deciding factors.
Depending on the layout of your walls (I will assume a square for now and not post-ten) you will get high restraint forces in your slab and walls (near the corners or any returns). Depending on the length of the building (if longer than 30-40m I would put a joint in the slab and walls and use some ancon dowels) but for discussion say 30m. I would full core fill the corners and put 1-3m of horizontal reo in to ensure that the wall doesn’t crack, (and all return walls).
Vertical joints in the walls can also help, will need a bit of extra reo in the slab at this points to stop reflection cracking, but I like to put some joints in the walls at corners if my wall length is above 20m.
Best to reinforce the slab as restraint to medium of high levels. Normally only a problem on the first two levels of your building then you’re sweet. To work out your restraint forces, there is a good bit of info in the PCI manual.
When in doubt, just take the next small step.