Nov 1, 2024 #1 H Howard David 1983 Structural Joined Nov 1, 2024 Messages 3 Do you stop slab reinforcing at controls joints (saw cut joints) in a slab on ground or allow the reinforcing to be continuous?
Do you stop slab reinforcing at controls joints (saw cut joints) in a slab on ground or allow the reinforcing to be continuous?
Nov 1, 2024 #2 jayrod12 Structural Joined Mar 8, 2011 Messages 6,304 Location CA We specify 50% continuous through the joints. Upvote 0 Downvote
Nov 1, 2024 Thread starter #3 H Howard David 1983 Structural Joined Nov 1, 2024 Messages 3 jayrod12 said: We specify 50% continuous through the joints. Click to expand... Do you see much cracking of the slab with this approach? Upvote 0 Downvote
jayrod12 said: We specify 50% continuous through the joints. Click to expand... Do you see much cracking of the slab with this approach?
Nov 1, 2024 #4 Once20036 Structural Joined Oct 7, 2008 Messages 533 Location US For us, it depends on the reinforcing. I`m OK with snipping 50% of the members in a wire mesh/fabric, but would be more accustomed to stopping rebar and using a dowel basket. Upvote 0 Downvote
For us, it depends on the reinforcing. I`m OK with snipping 50% of the members in a wire mesh/fabric, but would be more accustomed to stopping rebar and using a dowel basket.