As you say, a breaker "b" auxiliary contact interrupts the closing coil current when the breaker has closed, so there is normally no breaking duty on the pressure switch contact. The problem arises if the breaker does not close, say due to a mechanical hangup. The closing coil is normally not continuously rated and will burn to a crisp if it is kept energized for any extended period by the closed pressure switch contact.
"Normal" breaker control circuits would have momentary contacts doing the closing, and this is what I suggest that you consider - use the pressure switch to operate a one-shot auxiliary relay circuit, with a closed time of say 0.25 sec. The final control contact should be rated to interrupt the closing coil current in case the breaker hangs up (there are small control relays available to switch 10A @ 125 VDC).