Scotty, there was OLTC for more than 100 years.In 1910, ASEA came out with an OLTC called HM which was popular for many years.During the same period,American and English companies also had models of OLTC. It is true that MR was the first to develop high speed resistor type tapchangers.But almost all transformer companies had their own tap changer models.But the business setbacks in 1960's to 70's compelled transformer companies to stop manufacture of OLTCs and stick to their 'core competencies'.Last to do that was Elin in late90's.Today there are only two models or manufacturers with worldwide coverage -ABB &MR.Of course there are many manufacturers of OLTC in the emerging economies with various models.
Coming to Beengineers query -Dont worry nothing is going to happen.You have said that DGA of main tank oil is OK. It means either the device is DETC,but more probably the leakage is from the tap-selector tank of OLTC and not from the diverter switch tank( where arcing occurs).In 50's and 60's it was a practice of some customers to demand tap selector part also in a separate tank.You can verify this by having a look at the rating and connection diagram plate and also service manual ,if available.
Even if the minor leak is from arcing chamber,normally it will not cause much problem for short periods except for the nuisance of obscuring trf DGA analysis and need for filtering main tank oil after rectifying the leak.