Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

connecting / anchoring thick RC slab

Status
Not open for further replies.

mats12

Geotechnical
Dec 17, 2016
181
Hi guys. Im wondering how do you usually anchor new RC slab to existing when slabs are pretty thick (200 mm or more). I usually do anchoring in the middle of a slab, but since slabs are 200 mm thick I think its better idea to do anchoring in two rows like shown below:

sidra_naq8o3.png
 
Replies continue below

Recommended for you

Is this a slab-on-grade? Or a structural slab?

If on grade - we usually (always) use dowels in the center. If you get too close to the edge and some vertical shear is introduced, then you risk the top bars spalling out the concrete surface.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Why are we connecting them at all? if it is just to keep the edges together and no moment than do the middle, drilling and embedding things staggered just seem like we are bound to get close to the edge and spall/crack.
 
Presuming you have no need for moment transfer, I agree that centered reinforcing dowels are best. I see single-layer/centered reinforcing commonly for slabs even up to this thickness, at least for slab-on-grade not taking any moment. Only at 10" thick or thicker would I switch to top-&-bottom configuration (sorry for switching from mm to inches!).
 
Status
Not open for further replies.

Part and Inventory Search