lh:
You don’t give specific data on either the Ammonia vapor or the liquid, so I’ll have to resort to generalities.
The sparger you employ should be as efficient as you can buy or make. Sintered stainless steel in the form of a pipe would be my first choice. I’ve used it before and it worked very well when sparging the gas at the bottom of the receiver or tank. However, let’s be specific about the following:
The superheated ammonia vapor – as well as the supercooled ammonia liquid – have to be immaculately clean and free of any impurities, such as non-condensables, etc. In other words, you must ensure that the system obeys and follows the thermodynamic properties of PURE AMMONIA. Otherwise, I would not recommend you employ this system of cooling.
To determine the maximum quantity of NH3 superheated vapor that you can condense within the supercooled NH3 receiver or tank, you must make an accurate heat and mass balance around the system and the maximum quantity of superheated NH3 that you can put in it is dictated by the existing Maximum Allowable Working Pressure (MAWP) of your receiver or tank. In other words, what you are proposing is an adiabatic mix of these two fluids, with a resultant saturated NH3 liquid product. This is a BATCH operation and you cannot heat up the resultant saturated liquid any higher than that saturated temperature that corresponds to the saturated pressure equal to the MAWP of the receiver or tank. To do so, is to activate the NH3 safety relief valve that hopefully is installed and properly functioning on that same receiver or tank.
I have also used a similar technique on Ammonia 1st stage intercoolers on 2-stage Ammonia refrigeration cycles. The exceptions are that the end product is not a saturated liquid - but a saturated gas - and the process is continuous.
In order to make the heat and mass balance, you must accurately identify the quantity of supercooled NH3 liquid in the receiver or tank (your "heat sink") and be prepared to instantly shutoff the superheated vapor being sparged by using a sensitive and accurate pressure switch that is set at approximately 90% of the MAWP on the receiver or tank.
I would not run this operation without experienced engineering supervision.
I hope this helps answer your general questions.
Art Montemayor
Spring, TX