YKalaf, I cannot find my copies of ACI 506 specs/practice..but I do recall an older version I gave away stating that ACI 318 is the design method and it did not make a distinction between the dry or wet mix.
FYI, there are 3 companion documents for ACI 506...namely: 506R, 506.2 and 506.4R
An internet search indicates ACI 506R-90 (5.4.1) states reinforcement for shotcrete shall be designed per ACI 318.
Further Evidence:
In the last version of the UBC(97) according to Sec 1900.4.2 Shotcrete...it states" In addition to the requirements of Division II, design and construction of shotcrete structures shall meet the requirements of Division IV". Division II of the 97 UBC was essentially ACI 318-85 and Div IV is similar to IBC Sec 1914 and both are based on ACI 506.
Fast forward to the present. In the IBC-03, Sections 1901.2 and 1914.1 are the references stipulating ACI 318 be used for design...but as mentioned in previous post, amongst other things, IBC Sec 1914, modifies reinforcement requirements of ACI 318.