I'm not endorsing anything, but if they are going to hack off existing concrete and install new, require them to go after the old concrete with a steel brush to clear as much laitance as possible and follow as closely as they can the shear friction provisions for surface preparation (I don't see a 1/4" amplitude roughening of the column with all that rebar in there. You also want the surface wetted, before the new concrete is placed, as already mentioned here.
I would also suggest you re-check the bar placement for appropriate clearance between the bars based on the maximum aggregate size in the mix and get some cores. This column may not look crowded/congested but make sure it is not beyond 4% of the vertical cross-sectional area.
That said, the pour sequence looks odd. Did they pour the concrete into the column at the same time as the slab? Hence the void in the column and the void in the slab area as well? That doesn't sound like normal practice, particularly if the concrete column is higher strength concrete than the floor, unless they are pouring that high-strength puddle around the column at the floor level?
Brian