I have to disagree with Ron. Temperature monitoring is not expensive.
All it takes is a special thermocouple wire with the last 25 mm of the wire stripped and twisted together. This is imbedded in the concrete with the other end exposed. A reusable plug ($3 CDN each but not really essential) is attached that then plugs into the monitoring equipment. The monitoring equipment can be a simple reader ($200 CDN. for the simple readers. I have even seen digital multi meters that have the capability of giving temperature readings.) that gives a digital readout of temperatures or something that records the temperature over time. The wire is about $1 CDN per m. I usually recover whatever piece is sticking out of the concrete forms and reuse it several times until its too short to be useful.
When one considers the other costs in inspecting construction and the cost of poor quality construction these costs are insignificant.
It is usually only done in mass pours where the heat gain is a concern. In smaller pours where the thickness is less than 500 mm heat gain is not that much of a concern. It might also be done in high temperature conditions in southern climates but that’s something not usually a problem here in Canada.
Since these thermocouples are left in the concrete they could be used for long term monitoring. There is no concrete reason (pardon the pun) to monitor temperatures so this would be done for some other reason such as monitoring energy efficiency or some process reason.
Heat gain (called heat of hydration) occurs due to the chemical action in the curing of the concrete and can set up some thermal residual stresses in the concrete when it cools. These stresses then take up some of the available strength or can cause cracking in the concrete.
If the concern is freezing before the concrete cures, there are special thermometers available that will record the max and min temperature. These are twin tubes filled with mercury and then have a plug that stays at the top or bottom of the travel. The plug is reset by pushing a button and taping the thermometer so that the plugs move to the current temperature. These are normally placed inside the hording and simply left there until the hording is removed. I would consider the use of these to be normal due diligence in concrete work when freezing is a concern. These are inexpensive ($20 CDN or so each) Any concrete testing firm will have a supply of these.