If galvanising you just need to be careful with hydrogen emnbrittlement of higher strength rebar.
I once had a job where galvanised bars were snapping at a bend when they placed down cages, you could reproduce the issue if you hit the bar lightly with a hammer (think like slowly swinging a sledge hammer like you were putting a golf ball). Turned out it was a combination of the galvanising and the contractors fabricator incorrectly bending the bars (used a press suitable for bending flat plate vs correctly bending the bars around an appropriate diameter former). Either way it was amazing how you could simply snap a 500MPa bar like it was a twig. I've been wary of galvanising since, especially discouraging bending after the bars are galvanised, it can crack the galvanising and increases the hard working of bars that may have had some hydrogen embrittlement during the galvanising process.
Never used epoxy coated bars, they simply are not available in this part of the world, so correct cover and concrete mix and compaction for the win.
Almost every issue I've seen regarding longer term durability in existing structures has been due to inadequate cover to reinforcement and tie wires, contractors don't seem to appreciate the fact that there is a -0mm tolerance on covers, maybe its because they won't be around in 10/15/25 years when the problem rears its head. Engineers don't seem to appreciate that they need to provide sufficient tolerance, designing and drawing to 0mm tolerance simply isn't achievable for insitu construction.