Assuming that the column you are contemplating is the one shown in your last photo of the previous thread (as dik noted), you have to get back to basics.
Design considerations in reinforced concrete include much more than just the loading. As hokie66 noted, constructability has to be considered as well [highlight #FCE94F](hokie66:"The key to placement in columns is to leave plenty of space for placement and consolidation.").[/highlight] He is exactly right. This means that the size of the column has to accommodate placeability, the mix design must accommodate clearances and placement technique, the vibration scheme must accommodate the geometry of the column and the mix design, and the placement process, whether pumped, tremied or dropped must accommodate all of the above.
To give you an idea of clearance issues, the maximum size of the coarse aggregate in the mix ideally should not be more than 1/3 of the narrowest distance between the rebar. That means that if you are using typical 3/4" to 1" (19mm-25mm) coarse aggregate, you will have problems due to the congestion of rebar. Further, the minimum pump hose size will be on the order of 3" (75mm). It is not likely that you have those clearances based on the photo.
Have your concrete supplier design a mix for the clearances you have. Have your pumping subcontractor use a pump that will allow the hose to be deposited all the way to the bottom of the form, filling the form from the bottom without free-falling (dropping) the concrete (as Mike noted). Make sure that all the constituents of the concrete mix are properly done...saturated aggregates, proper compensation for water, proper admixtures and admixture dosing. Then make sure that you have adequate quantity and wand length for the vibrators to be able to properly consolidate the concrete. Don't vibrate the forms, but you can tap the forms with hammers to allow release of entrapped air.
Good luck.