Typically foundation is poured first and then concrete pedestals (see attached sketch). How is shear checked in this construction joint?
Thanks,
iv
 
i have yet to see a program excel or software that has an option to consider the effects of construction joint between pedestal and footing. i'm interested to know the effects as well if there is any.
 
iv63 - ron9876 has already answered your question. You may also refer to solved example - Design for Transfer of Horizontal Force at Base of Column given in Notes on ACI 318 and published by PCA.
 
See example 22.6 - "Design of Transfer Horizontal Force at Base Column" from PCA/ACI 318-05 Notes.
 