Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

What is considered Supplementary Reinforcement for anchorage design in reinforced concrete pedestal

oengineer

Structural
Joined
Apr 25, 2011
Messages
740
Location
US
If I have a pedestal that is 24"x24" with (16)-#6 vertical rebar & #3@8'o.c., would both the vertical rebar & ties be considered as Supplementary Reinforcement?

The code mentions the use of stirrups (See ACI 318-19 Section 17.7.2.5.1). How would stirrups be considered for a pedestal? I would think only ties would be used for pedestals.

1752095299968.png

1752095483429.png

Comments/suggestions are appreciated.
 
You need to get a development length of the stirrup which is difficult in a pedestal. I always recommend Design of anchor reinforcement in concrete pedestals by Widianto, Patel and Owen as a reference. You can find it online. Below is an except. Or ASCE's Anchorage Design for Petrochemical Facilities is a good reference.

Screenshot.png
 
Are you talking about anchor reinforcement or supplementary reinforcement?

Supplementary reinforcement should generally look like the layout of anchor reinforcement, but they do not need to be developed.
 
I've taken supplementary reinforcement in your case as being the ties, which also need to be restrained by something. So rarely is there supplementary bar in a pedestal
 