ajk1 said:
Gilbert seems to be saying that only closed stirrups are satisfactory. There are a lot of non-edge beams in non-seismic areas that have performed entirely satisfactorily over 100 years or more, where the stirrups are not closed.
You're preaching to the choir here. To clarify my understanding of Gilberts stuff, he's only saying that open stirrups are undesirable when ductility is required.
ajk1 said:
when you say "durability" do you mean "ductility"?
Yup. Obviously, there are no beams for which durability is not required.
ajk1 said:
I don'like the lapped stirrup. Seems to introduce extra field work to tie the stirrup up vertically so it is lapped; potential for field errors. I have a feeling that laps should be avoided if possible.
I don't have a problem with it for low ductility and have had contractors request this on numerous occasions, particularly for deep, narrow beam construction.
ajk said:
Like you, I never heard of break-out of concrete in the lower re-entrant corner as shown in your diagram
Ditto. I hate to use the contractor "I've always done it this way..." argument though. Makes me feel like a hypocrite. That said, anecdotal evidence is a valid, if weaker form of evidence than experimental evidence. Were one to consider this in more detail, additional beneficial factors would come to light:
1) The compression fields coming in from the hogged slab via flexure and shear will improve matters.
2) The outward hook detail requires a longitudinal hanger bar which changes the mechanism substantially. Less outward thrust and closer to to pushing straight down.
ajk1 said:
None of my comments should be taken as "Canadian" or even "Ontario" practice. Parts of Canada are in significant seismic areas.
In my opinion, discussion of this detail cannot be had meaningfully
unless you tag it as aseismic/low-ductility.
1) If this is a gravity only beam in Vancouver, outward 90's are okay.
2) If this is a moment frame beam in Vancouver, outward 90's are absolutely NOT okay.
3) Really, if this is a moment frame beam
anywhere, outward 90's are probably ill-advised as they will not offer buckling restraint to the top bars.
ajk1 said:
Why? Maybe he is thinking of seismic regions?
I would bet a thumb that it is for the reason shown below.