Depends how your Coriolis meter was used and what type it is.
Two approachs:
1) Predictive: batch blend ratio determination
2) Feedback: density measurement.
I have seen installations (in pharmaceutical plant) that used upto three mass flow meters, one used as density, and a storage tank and had to use very high quality raw caustic all swept away and replaced with a single fork or tube density meter and a control valve, and with less expensive raw caustic (because of relaxing the specification).
In one system i saw two mass meters were used predictively i.e. they batched water and strong casutic nto the tank in a proportion based on the target quality and the known quality of the strong caustic.
At the storage tank the mix (exothermic) was recirculated through a third mass meter to look at the density.
This system was replaced with a single density meter.
The two flow streams, each with a flow control valve (to maintain the master stream constant and match the other to it) are pipeline mixed using a static mixer. The density meter is downstream of the static mixer and controls the slave stream control valve.
The density meter has on-node calculation of %concentration.
The calculation steps are:
measure density of the mix and the temperature.
Using matrix-referral (i.e. stored curves of temperature Vs density for different concentrations) the density at 15degC is found.
The next step is to calculate the concentration from the density at 15degC. though some operators simply apply a linear scale to the 4-20mA output, where concetration is not linear with density correction algorithms can be programmed. (rarely necessary with caustic).
A caution, in feedback control using mass meters mass meters are optimised for mass flow determination and exploit the variation in resonant frequency of operation with density to provide a density measurement.
A dedicated density meter is optimised in its design for density measurement. They also have sophisticated algorithms and more extensive calibration.
The diference is in the accuracy. Micro-Motion Elite (Emerson) mass meters claim density accuracy equivalent to the Solartron fiscal density tube (at predetermined conditions?) but most other mass meters fall far short of this performance.
Feedback control allows you to relax the specification for the strong caustic and pay less because any variation in its quality is automatically corrected for. In the batch blend method the blend ratio is predicted assuming a known and constant quality of the raw caustic.
In the single instrument feedback approach you can blend on demand without an intermediate 23% storage tank. This also allows you to change the target quality at will.
You can also duplicate this control at point of use by providing a ring main for raw cautic to citical useage points where point of use on demand blending can be performed.
You must decide the accuracy you need
for the concentration measurement and compare options and prices accordingly and decide on the method.
You must then look for appropriate measurement techniques which could be density and compare technologies.
JMW