I know that this post is fairly old, but it caught my eye when it popped up in a related Google search. I’d like to comment on zazmat’s post.
The advantage is that it is physically and electrically smaller than the Y/broken delta, so should be less expensive.
I am not sure that one thing can be electrically smaller than another.
The disadvantage is that there are only a couple of manufacturers, and UL/CSA is not always available.
Resistance grounding is more and more common today than in the past; zigzag-transformer manufacturers have responded in kind. In my experience, and my colleague’s experience, zigzag transformers have been made readily available to us with or without CSA certification.
Also, zigzags only create neutral, so for a 4160V system, the neutral point would be 2400V. You could not add a 59 relay to this resistor or pulse to locate ground faults.
This is untrue. The CEC specifically allows for an alarming system of up to 5 kV.
Canadian Electrical Code, Part One, 2006 - 10-1102 (2)
“Where line-to-neutral loads are not served, provision shall be made to automatically de-energize the system on the detection of a ground fault unless the electrical system is operating at 5 kV or less, in which case it shall be permitted to remain energized on the detection of a ground fault provided that
[ol a][li]The ground fault current is controlled at 10 A or less; and[/li]
[li]A visual and/or audible alarm is provided to indicate clearly the presence of a ground fault.[/li][/ol]
Article 250.36 of the NEC does not address systems above 1000 V and Article 250.186 does not require that an impedance-grounded system be a tripping system. What code dictates that the 4160-V system referenced above cannot be an alarming one? The use of an appropriate neutral-grounding-resistor monitor provides both 51N and 59N protection.
With regard to your question SudionoSu, it is worth mentioning that should the resistor across the broken-delta transformer fail, all 67N and 51N relays will fail to function. It is with this point that I address Rodmcm’s original question that began this thread.
The resistor’s continuity cannot be monitored when installed in a broken-delta configuration. If the resistor fails, current-sensing protection can no longer function; an important consideration. Choosing a zigzag transformer for resistance grounding allows for the use of a neutral-grounding-resistor monitor. Below is a link to a paper with additional information on the subject.
Monitoring Neutral-Grounding Resistors - An Update
---
Cory Anderson