dithomas
Electrical
- Oct 18, 2002
- 74
I am searching for a way to determine the losses on 40 year old Federal Pacific 1000kVA 13.8kV - 480 delta delta transformers in order to compare them to a new modern transformer. A saving in operating cost could justify replacing the 14 FPE transformers with new Delta Wye units.
There are 14 transformers in groups on various 13.8KV circuit. An example is one circuit with four transformers on the same 13.8kV feeder. there is no metering on each transformer primary only the Eaton IQ4000 at the 13.8kV breaker. The load on each transformers is approximately a 500 amp steady load. This has been the loading for the entire life of the transformers.
Is there a way to determine the losses on one transformer?
The four single ended unit substations have tie breakers and a bus tie between them and can be paralleled to share load and one if the four transformers can be unloaded.
Any ideas? Thank you in advance.
There are 14 transformers in groups on various 13.8KV circuit. An example is one circuit with four transformers on the same 13.8kV feeder. there is no metering on each transformer primary only the Eaton IQ4000 at the 13.8kV breaker. The load on each transformers is approximately a 500 amp steady load. This has been the loading for the entire life of the transformers.
Is there a way to determine the losses on one transformer?
The four single ended unit substations have tie breakers and a bus tie between them and can be paralleled to share load and one if the four transformers can be unloaded.
Any ideas? Thank you in advance.