combined footing vs strap (tied) footing

Status
Not open for further replies.

delagina

Structural
Joined
Sep 18, 2010
Messages
1,008
Location
US
i believe combined is more appropriate here as oppose to strap.
am i right?

i read strap is used if footings are farther apart. but distance is subjective.

any advice.

thanks,
 
I usually use a combined footing if the columns are that close. I've actually used combined footings when the columns were much further apart than that.

I have a spread sheet that I wrote that covers the design of these footings making them very ease to design. Maybe that's why I like to use combined footings.
 
I usually just check the bearing pressure under the footing. Bearing should be related to this pressure. Whether or not you want to allow the resultant to end up outside the middle 1/3 of the footing is up to you.

Also, the spreadsheet I wrote does not allow for shears or moments to be applied in two directions.
 
Once you have you bearing pressure distribution that you show in your attachment. Just draw the FBD with the column loads and the bearing pressure from that you can draw your shear and moment diagrams.

Then design for the critical negative and positive moments. Check the shear and that is it.
 
I've been in a company with a guideline to always have 100% bearing area.

That's why I'm interested if there is any publication out there that discuss this.

Or this is just an engineer preference.
 
For lateral loads I am fine using anything that doesn't exceed the allowable bearing pressure. The 0.6D load cases give the safety factor
 
As ash060 states, the 0.6D case can cause some problems. Many engineers will tell you to make sure you have 100% bearing under the footing. This has caused problems for me with the design of footings in the past. It would be your decision as the EOR (or your boss) of what you are comfortable with.
 