Column Stiffness Modifier - Slab Deflections

Status
Not open for further replies.

Drapes

Structural
Oct 27, 2012
97
What stiffness modifiers, if any, are recommended for concrete columns when designing a slab for deflections (i.e. under service loads)? Using a non-linear cracked section analysis program like SAFE, obviously the slab stiffness is inherently accounted for, so I have no issues in capturing this. But I am unclear on what to use for the column stiffness.

I understand that under ultimate gravity loads, a stiffness modifier of b/w 0.7Ig and 1.0Ig is used for columns depending on the axial load (low rise vs high rise structure), although from a punching shear point of view, the general consensus is to take 1.0Ig.

Is it reasonable to take a column stiffness value of 1.0Ig under serviceability conditions as well? Or is that being too unconservative?

 
Replies continue below

Recommended for you

Here's an approach:

1. Assume Ig for your columns
2. Run a service-level analysis using alternating live loads
3. Get the associated column axial and bending moments for each combination
4. Check for cracking using: f = P/A + My/Ig

If the column cracks (compared to fr = 7.5 x Sqrt(f'c), or perhaps assume a more conservative value of 5.5 x Sqrt(f'c):
1. Use the 0.7Ig or
2. Calculate an Ie directly (more work without much gain I think).

Or you could just assume 0.7Ig and go with it - getting perhaps a conservatively higher value of slab deflections than the more rigorous analysis would get you.


Check out Eng-Tips Forum's Policies here:
faq731-376
 
I would use caution with this approach when it comes to designing for punching shear in the slab. I would recommend using 1.0 Ig (lowest I would personally go is 0.7 Ig) and ensure that you don't have punching shear issues.
 
Agree
I was speaking only for the slab design checks for deflection and strength. For the punching shear you want to stay on the conservative side which means 1.0Ig for the column.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Thanks for the feedback JAE and slickdeals
 