Again, generally
For 208/120V systems: Black, Red, Blue for A,B,C phases
For 480/277V systems: Brown, Orange, Yellow for A,B,C phases
No code for most conductors except ground, neutral (as stated) and then some other "oddball" applications.
For an isolated power system in a health care facility, orange, brown and yellow are required for the isolated conductors. Article 517
110.15 High-Leg Marking.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded to supply lighting and similar loads, the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means.
424.35 Marking of Heating Cables.
Each unit shall be marked with the identifying name or identification symbol, catalog number, and ratings in volts and watts or in volts and amperes.
Each unit length of heating cable shall have a permanent legible marking on each nonheating lead located within 75 mm (3 in.) of the terminal end. The lead wire shall have the following color identification to indicate the circuit voltage on which it is to be used:
(1) 120 volt, nominal — yellow
(2) 208 volt, nominal — blue
(3) 240 volt, nominal — red
(4) 277 volt, nominal — brown
(5) 480 volt, nominal — orange