On a related note, I had a contractor call me today saying that the concrete they were pouring set up within 30 min, and did not allow for them to install dowel rods and anchor bolts for columns. They were complaining about the concrete specs, specifically the w/c ratio, which was 0.4.
The mix design they provided had 564# cement, 262# water, and they added accelerator due to cold weather. Slump of 4 was specified
My first thought was that the concrete took too long to get to the site, or they added too much accelerator, but I find it hard to believe that if they sampled the slump on site and got 4", that it would have set up in 30 min. any thoughts?? I dont think that the w/c ratio is an issue, since higher strength concrete is typically limited to this ratio, and also that ACI recommends lower wc ratios for cold weather.