Dear All,
Thank you for sharing your learned opinion on point A3. See my mail dated 9th Oct.
I try to go through it and see whether it make sense?
1. the relay coil rated 12Vdc Ri=80 Ohm is connected across a 12Vdc source. A reversed diode (only) is connected across the coil. When the source is off, voltage across the coil is 0V, I=0A, N.O. contact is in open position,
1.1 when the 12V source is switched on, the [transient voltage] across the coil [begins to rise] from 0V to 12V. After a short time delay (depending on L/R)* when the voltage reaches 8.4V; the relay picks up. The N.O. contact closes. However, the voltage continues to increase passing 8.4V and finally reached [steady voltage] 12V. At 12V, the steady current(coil) I=12V/80 Ohm = 0.15A , Power (coil)=I2 x Ri = 1.8W. Current flow through the reversed diode is +- =0A , Power (diode)=0W. This state continues until the source is [switched off], see 2,
2. When the 12V source is [switched off] with the (coil steady voltage) at 12V, the [generated back emf] is dependent on L di/dt. It is possible to >12V. Therefore, the [transient current] due to the back emf is possible to > 0.15A. As the only resistance is Ri, while the diode forward resistance is +- 0 Ohm,
2.1 When the 12V source is [switched off], the coil voltage from steady 12V starts [to decrease] (depending on R/L)** from 12V to 0V. The only resistance is Ri=80 Ohm. At 1.2V the relay releases (= drop-out) i.e. the N.O. contact resets to the open state. When the [diode is in series] with a resistor Rs, see 3,
3. The coil voltage from 12V would [decrease at a slower rate] (depending on R/L)**. The resistance would be =(Ri + Rs). The voltage would take a longer time to decrease from 12V to 1.2V, i.e. the N.O. contact drop-out at a longer time delay.
Che Kuan Yau (Singapore)