Code Requirement for Control Ground

Status
Not open for further replies.

MNMaint

Mechanical
Jan 20, 2009
13
Hello,
I have an installation where shielded 18/2 cable was used to deliver 24V power to a control actuator. The installer used the shield as the ground.

Is this code compliant?
If so, is it otherwise acceptable?

Thank you
 
Replies continue below

Recommended for you

Is your control circuit required to be grounded? Many (possibly most) are not. Typically, we might find isolated two-wire control circuits run exactly as you describe, with the shield grounded at one end only.

If you describe your circuit in much greater detail, you might get a more thorough answer...

Good on ya,

Goober Dave
 
Sounds similiar to a question I had:

thread248-279001
 