BIMR - That is correct, there would represent a step to finish grade outside. However I've come across ways around this.
All,
I actually found the reference in the code that I was looking for and thought I would share:
2012 IBC 2304.11.2.2 - "Wood supported by exterior foundation walls. Wood framing members, including wood sheathing, that rest on exterior foundation walls and are less than 8 inches (203 mm) from exposed earth shall be of naturally durable or preservative-treated wood"
2013 CBC 2304.11.22 - "Wood supported by exterior foundation walls. Wood framing members, including wood sheathing, that rest on exterior foundation walls and are less than 8 inches (203 mm) from exposed earth shall be of naturally durable or preservative-treated wood" - California however does have the exception for DSA-SS and OSHPD 1, 2 &4, "At exterior walls where the earth is paved with an asphalt or concrete slab at least 18 inches (457 mmm) wide and draining away from the building, the bottom of the sills are permitted to be 6 inches (152 mmm) above the top of such slab. Other equivalent means of termite and decay protection may be accepted by the enforcement agency"
Depending on the project, where I've come across it is via the height separation of 6 or 8 inches. I've also seen where a stem wall is introduced as part of the foundation to raise the sill plate elevation. In situations where you are flushed with outside grade, that is where alternates as pressure treated wood, or even non-wood construction are considered. I've attached a sketch from one of my recent projects. In this case, the red annotations were only trying to convey the height differential to another team member if we had wood construction. The project itself was not using wood for this installation.