rcw retired EE
Electrical
- Jul 21, 2005
- 907
Our client is requiring each "switchgear cubicle and MCC cabinet" to have automatic CO2 fire suppression. That means a detector and a discharge nozzle in each "cubicle".
Has anyone ever seen 15 kV or 600V switchgear or MCC's with CO2 protection? Not an electrical room with a Halon or CO2 flood system, but CO2 piped to each switchgear section.
My initial reaction is that all of the CO2 piping and detector wiring will cause more problems than the CO2 cures. (I have repaired switchgear faults caused by fire detection equipment.)
I believe this is from an insurance company's misinterpretation of NFPA 850 7.8.1.3
Has anyone ever seen 15 kV or 600V switchgear or MCC's with CO2 protection? Not an electrical room with a Halon or CO2 flood system, but CO2 piped to each switchgear section.
My initial reaction is that all of the CO2 piping and detector wiring will cause more problems than the CO2 cures. (I have repaired switchgear faults caused by fire detection equipment.)
I believe this is from an insurance company's misinterpretation of NFPA 850 7.8.1.3