Comment on ScottyUK (Electrical) May 4, 2004 marked ///\\Hi jB,
Your statement is true up to a certain point, but most CBs have a high-set function for which the tripping time is not clearly defined.
///Yes, below .o1 sec. Such devices can only be coordinated on enegetical basis needed for tripping, if electromagnetic and if electronic, then there is the short-time delay setting of upstream breaker serving as a backup of the downstream instantaneous setting of breaker or protecting cable between load side of upstream breaker to the line side of downstream breaker(s).\\ A heavy fault may well cause the high-set function of both the upstream and downstream CBs to operate, giving a 'race' condition where both CBs see the fault and react to it by initiating a trip.
///Yes, this is true for the circuit breakers that have no electronic trip unit, e.g. GE MicroVersaTrip, Square D Micrologic, Cutler-Hammer Digitrip, Siemens SensiTrip, etc. and those electromechanical breakers that have the same t*I*I peak through.\\ The high-set function is 'instantaneous' in so far as real world apparatus ever can be instantaneous, and this makes grading between devices impossible unless the downstream high-set level can be set to a level which allows the downstream CB to clear a fault while the upstream CB is on the I-t curve.
///Yes, this is still possible to see, engineer and design. However, the technology is there to avoid it. I always try to avoid it (even if it costs more money).\\ Some of the larger and more expensive CBs allow the high-set to be turned off, which makes this possible.
///Nowadays, even the small CB three phase circuit breaker from about 3A up, see GE site for breakers.\\I thought the US used standard curves - ANSI? - for the responses of protection relays.
///Yes, mostly for electromechanic and solid state. However, the integrated digital relays do seem to have various algorithms and logic for the more sophisticated protection.\\ Does this apply to breakers as well? In IEC land, we find it easy to grade CBs from different manufacturers because they all conform to standard curves defined in BS7671 as Types B, C, & D up to a certain size. Larger breakers have their own means of 'bending' their response curve to suit the application, rather than a set of pre-defined curves. HV curves are defined in a standard whose number eludes me but are known as: EI - extremely inverse; VI - very inverse; SI - stanadrd inverse.
///The electronic trip units marketed worldwide, e.g. Schneider Electric / Square D do use the long time setting, long time delay, short time setting, short time delay, ground fault, t*I*I, and instantaneous setting.\\\