Circuit Breakers Used as Switches

Status
Not open for further replies.

tandyn

Electrical
Oct 28, 2008
2
Can a larger circuit breaker be used as a switch on a fused circuit sized for a lower current?

i.e. a 70A breaker used as a switch on a circuit fused and sized for 40A
 
Replies continue below

Recommended for you

To clarify, is this allowed by NEC?
 
Yes, as long as the circuit conductors are protected by the upstream fuse, I believe this would be allowed.

I await enlightenment from one our "code lawyers".
 
Assuming you are in North America...

A Molded Case Circuit Breaker (MCCB) would need to be labeled "SWD" for switching duty I believe, but as far as I know, almost all new MCCBs are now labeled as such. But the term "circuit breaker" is a little nebulous now with the advent of what are called "Mini Circuit Breakers" or MCB from IEC countries. I do not believe they are going to be labeled to be used as switches.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376
 