Circuit Breaker Sizing for 30 KW Motor 1
tahirinst
IQ
I need to install circuit breaker on 3 Phase Motor ( 30 KW). This motor is installed at Screw air compressor ( direct coupled). Motor voltage 400VAC, 50 Hz
Please advise size of breaker which should be installed. Motor Name Plate data is attached.
 http://files.engineering.com/getfile.aspx?folder=9e970a64-70b2-4127-b915-648d87f65459&file=Motor_Name_plate_data.jpg
In North America that is a matter of code compliance.
We reach for the Electrical Code book.
For DOL starting of a squirrel cage induction motor the code maximum is 250% of rated current with exceptions.
Consult your local code.
Bill
"Why not the best?"
Jimmy Carter
Hi tahirinst,
Are you sizing the CB that feeds the Air Compressor's Panel Board or the CB that will directly feed the motor?
Maybe a single line diagram will help us understand your requeriments
Regards.
JBC
"The more I read, the more I acquire, the more certain I am that I know nothing"
CB will directly feed the three phase motor.....
Tah: If you are not using a contactor+relay scheme, you should use a "Motor Circuit Breaker" that has Thermal+Magnetic protection
You can just select it from a catalogue (i attach an example)
BEWARE: The rated Volts/frecuency/kA Icu must be in accordance with your installation
JBC
 http://files.engineering.com/getfile.aspx?folder=8ed731ee-c453-463f-aa3e-5100b614b4ec&file=GV3P.png