Martinelli21
Electrical
- May 31, 2005
- 4
I have a 6600 to 380 VAC, 250 KVA transformer supplying a motor control center with a 600A breaker on the secondary side. If a bolted short circuit occurs at one of the motor terminals, will the breaker in the MCC bucket trip before the breaker at the transformer? Do I assume 9500A applied to both breakers instantaneously? Or since the motor circuit protector in the MCC is set to trip at 300A and the magentic setting of the transformer breaker is 3000A, will the MCC breaker trip before the transformer breaker? I would like to stay with thermal-magnetic breakers and I'd rather not use electronic breakers and the short time-delay feature.