How much voltage dip does your system allow? If these motors start at the same time, you may need larger genset (830kVA) or if they can be staggered you may need around 400 kVA!Bab AK (Electrical)(OP) said:Here we have 5 set of 55 KW inductive motors running DOL, I want to choose a diesel generator to feed all of them and provide their starting parameters, our derating factor here is about 20%. How much would be the right size in KW approximately?
You are safer to use KVA or Amperes to size a generator.OP said:And also the base loud is 65 KW ( 50 KW lighting and 15 KW panels, PLC, office small loads )