Hello yfuo28,
There are more parameters than you think, it affects chiller performance directly and indirectly.
Firstly, air temperature is the parameter that you should think since your water circuit is cooled with air. As air temperature is low, chiller performance is increasing because colder air cools more, it is simple. As air temperature is increasing, chiller performance gets worse. There is usually a restriction in air maximum temperature that you should take into the consideration. When air temperature reaches the max. value for chiller, chiller stops working since the pressure in evaporator is high. The max. air temperature will be written in the product catalogue. This is important. Keep in mind!
Secondly, cooled water temperatures are the parameters that you design. (for example, 6/12oC, 8/14oC) These values also affect chiller performance because of LMTD (log mean temperature difference). I strongly suggest you to search LMTD phenomenon.
Thirdly, chiller installation is another important issue, you can easily find the suggestions from catalogue.
Finally, altitude is another parameter that you consider since it affects the atmospheric pressure. When seleceting chiller, you shoulg give that data to vendor.
I hope these give you an idea. These topics are very interesting and enjoyable to search.
Regards,
Emre