Hello, I have read several eng-tips forums over the past year and they are very helpful, recently I have read choked flow related questions and answers.
I have been trying to determine the effect of stacks on a large propane tank pressure relief valve(s) (2 inch relief valves and stacks: API equivalent relief valve size is smaller than 2 inches).
I am curious as to what happens with a spring PRV that is combined with a stack.
Without the stack, I know there will be choked flow. During a relief situation psia is >265 and is relieved to atmosphere.
With the stack I believe there will still be choked flow, but I am unsure exactly where this is happening and what effect the stack may have. The main goal is to determine if the stack reduces flow rate by any significant amount. Let's define significant as about 1%.
My guess is that with the stack there will be choked flow across the PRV and what happens in the stack has no effect. However, the problem I have is when I try to think of velocities and pressures throughout the flow:
as I understand it, the pressure from the tank can only drop by about 50% maximum through a choked flow. If that is the case, then the pressure in the stack is still well above atmospheric. If this is the case the pressure in the stack would be about 130 psia and could not decrease by much without increasing the velocity of fluid (which I believe is not allowed to be greater than Mach 1). This would mean that at the exit of the stack, the pressure drop would again be great enough as to induce choked flow again.
Overall, I think that the PRV is the limiting factor and that putting the stack on has little if anything. However, I cannot seem to explain why.
If anybody can explain to me what exactly would be happening and explain the pressure at the different points in the system I would greatly appreciate it.
Thanks
I have been trying to determine the effect of stacks on a large propane tank pressure relief valve(s) (2 inch relief valves and stacks: API equivalent relief valve size is smaller than 2 inches).
I am curious as to what happens with a spring PRV that is combined with a stack.
Without the stack, I know there will be choked flow. During a relief situation psia is >265 and is relieved to atmosphere.
With the stack I believe there will still be choked flow, but I am unsure exactly where this is happening and what effect the stack may have. The main goal is to determine if the stack reduces flow rate by any significant amount. Let's define significant as about 1%.
My guess is that with the stack there will be choked flow across the PRV and what happens in the stack has no effect. However, the problem I have is when I try to think of velocities and pressures throughout the flow:
as I understand it, the pressure from the tank can only drop by about 50% maximum through a choked flow. If that is the case, then the pressure in the stack is still well above atmospheric. If this is the case the pressure in the stack would be about 130 psia and could not decrease by much without increasing the velocity of fluid (which I believe is not allowed to be greater than Mach 1). This would mean that at the exit of the stack, the pressure drop would again be great enough as to induce choked flow again.
Overall, I think that the PRV is the limiting factor and that putting the stack on has little if anything. However, I cannot seem to explain why.
If anybody can explain to me what exactly would be happening and explain the pressure at the different points in the system I would greatly appreciate it.