Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Chilled water system - pump head

Status
Not open for further replies.

Hassanakhlaq

Mechanical
Joined
Jan 13, 2009
Messages
6
Location
SA
While calculating the pump head in a closed loop chilled water system, we need to determine the total friction losses that a pump is supposed to overcome in the piping loop.For this purpose only supply line upto the coil (AHU / FCU etc) should be taken in account or return line from coil back to the pump should also be considered.Or in other words equivalent length of the critical path comprises of both supply and return piping length or only length of the supply line upto the coil.Thanks
 
Hassanakhlaq,

All pipe will have water flowing thru it from the pump -- so all pipe must be counted (supply plus return).

Don't forget the coil and control valve drops, and if you're using balancing valves, they need some DP also.

Good on ya,

Goober Dave

 
DRW is right, you need to take both the delivery part and the return circuit into consideration.

Also consider that if there are multiple "loops" possible serving different cooling coils, ensure you are analyzing the one that has the largest head loss, this is typically the longest or the furthest away from your pump.

this message has been approved for citizen to elect kepharda 2008
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top