As many would already know i am writing some notes on an undergrad manual that will go in the FAQ, the next chapter has some simple properties of concrete. These are from notes i have taken over time, two or more are from posts in this forum, other are from the net.![[bigears] [bigears] [bigears]](/data/assets/smilies/bigears.gif)
If you have the time please look through them and comment on anything you do not agree with.
Or if you have any properties that you think should be apart of this list, please post.
Properties
1. Temperature and shrinkage causes tensile forces in concrete, due to the interaction of reinforcement and concrete; Cracking levels depend on,
a) Tensile strength of concrete.
b) The cover thickness.
c) The diameter of rebar
d) Rate of corrosion.
2. Poisson’s ratio: A value of about 0.2 is usually considered for design.
3. Shear strength: The strength of concrete in PURE SHEAR has been reported to be in the range of 10 to 20% of its compressive strength.
4. Factors influencing creep:
Creep increases when,
a) Cement content is high,
b) w/c ratio is high,
c) Aggregate content is low,
d) Air entertainment is high,
e) Relative humidity is low,
f) Temperature (causing moisture loss) is high,
g) Size / thickness of the member is small,
h) Loading occurs at an early age &
i) loading is sustained over a long period.
5. Effect of creep:
Detrimental results in RC structures due to creep:
a) Increased deflection of beams and slabs.
b) Increased deflection of slender columns (possibly leading to buckling)
c) Gradual transfer of load from concrete to reinforcing steel in compression members.
d) Loss of prestress in prestressed concrete.
6. In order to reduce the effect of creep-deflection it is advisable to use 0.2% of cross sectional area at the compression face.
7. Symmetrical arrangements of reinforcement will aid to avoid the differential restraint.
8. Reduction of moments on account of moment redistribution is generally NOT APPLIED TO COLUMNS.
9. Reinforcement availability:
Standard diameter sizes (mm): 6, 8, 10, 12, 16, 20, 24, 32, 40
Standard lengths: > 12mm diameter: 12 metres
< 12mm diameter: from a coil
10. These values are approximate and should be used only as a check on the total estimated quantity:
Slabs - 80 - 110 kg/m3 (flat slab120-220kg/m3)
Columns - 200 - 450 kg/m3
Walls - 40 - 100 kg/m3
R/C footings 70-90 kg/m3
Pile caps - 110 - 150 kg/m3
Rafts - 60 - 70 kg/m3
Beams - 150 - 220 kg/m3
Transfer slabs 150kg/m3
Retaining walls-110kg/m3
Stairs – 135kg/m3
Note: The actual reinforcement quantity in the element will vary according to detailing practice and efficiency of the concrete element.
11. In normal circumstances and where N grad concrete is used, forms may generally be removed after the expiry of the following periods:
Type of Form Work (Location) Min period before striking Form Work
a) Vertical formwork to columns, Walls, beam 16 - 24 hrs
b) Soffit formwork to slabs (props to be re-fixed immediately after removal of formwork) 3 days
c) Soffit formwork to beams (props to be re-fixed immediately after removal of formwork) 7 days
d) Props to slabs: (1) Spanning up to 4.5m 7 days (2) Spanning Over 4.5m 14 days
e) Props to beams & arches
1) Spanning up to 6m 14 days (2) Spanning Over 6m 21 days
12. CONCRETE MIX RULES OF THUMB
• ADDING 3L OF WATER TO ONE CUBIC METER OF FRESHLY MIXED CONCRETE WILL:
a. Increase slump about 25mm
b. Decrease compressive strength about 1 to 2 mPai
c. Increase shrinkage potential about 10%
d. Waste as much as 1/4 bag of cement
• IF FRESHLY MIXED CONCRETE TEMPERATURE INCREASES 10 DEGREES:
a. About 3L OF WATER TO ONE CUBIC METER maintains equal slump
b. Air content decreases about 1%
c. Compressive strength decreases about .5 to 1.2 mPai
• IF THE AIR CONTENT OF FRESHLY MIXED CONCRETE:
a. Increases 1%, then compressive strength decreases about 5%
b. Decreases 1%, then slump decreases about 10mm
c. Decreases 1%, then durability decreases about 10%
13. The main components of cast-in-place concrete floor systems are concrete, reinforcement (normal and/or post-tensioned), and formwork. The cost of the concrete, including placing and finishing, usually accounts for about 30% to 35% of the overall cost of the floor system.
14. Where normal 500 mPa reinforcement is utilized, a concrete mix with a compressive strength of 32mPa yields the least expensive system.
15. Where post-tensioned reinforcement is used, a concrete compressive strength of at least 40mPa psi is usually specified to attain, among other things, more cost-effective anchorages and higher resistance intension and shear.
16. Having the greatest influence on the overall cost of the floor system is the formwork, which is about 45% to 55% of the total cost.
Three basic principles govern formwork economy for site-cast concrete structures:
• Specify readily available standard form sizes. This is essential to achieve economical formwork. Most projects do not have the budget to accommodate custom forms, unless they are required in a quantity that allows mass production.
• Repeat sizes and shapes of the concrete members wherever possible. Repetition allows forms to be reused from bay to bay and from floor to floor, resulting in maximum overall savings.
• Strive for simple formwork. There are countless variables that must be evaluated and then integrated into the design of a building. Economy has traditionally meant a time-consuming search for ways to reduce the quantities of materials. For example, it may seem appropriate to vary the depth of beams with the loading and span variations, providing shallower beams where the loads or spans are smaller. This approach would result in moderate savings in materials, but would create additional costs in formwork, resulting in a substantially more expensive structure—quite the opposite effect of that intended. Providing a constant beam depth while varying the amounts of reinforcement along the span length is the simplest and most cost-effective solution.
17. ABRASIVE RESISTANCE of concrete increases with compressive strength and use of aggregate having low abrasion.
18. Do you know that:
For steel bars to lose one mm diameter due to corrosion, it takes about 12.5 years. But due to practical reasons the number of years reduces due to hostile corrosive environment. For 6mm dia To corrode completely it takes about 75 years.
When in doubt, just take the next small step.
![[bigears] [bigears] [bigears]](/data/assets/smilies/bigears.gif)
If you have the time please look through them and comment on anything you do not agree with.
Or if you have any properties that you think should be apart of this list, please post.
Properties
1. Temperature and shrinkage causes tensile forces in concrete, due to the interaction of reinforcement and concrete; Cracking levels depend on,
a) Tensile strength of concrete.
b) The cover thickness.
c) The diameter of rebar
d) Rate of corrosion.
2. Poisson’s ratio: A value of about 0.2 is usually considered for design.
3. Shear strength: The strength of concrete in PURE SHEAR has been reported to be in the range of 10 to 20% of its compressive strength.
4. Factors influencing creep:
Creep increases when,
a) Cement content is high,
b) w/c ratio is high,
c) Aggregate content is low,
d) Air entertainment is high,
e) Relative humidity is low,
f) Temperature (causing moisture loss) is high,
g) Size / thickness of the member is small,
h) Loading occurs at an early age &
i) loading is sustained over a long period.
5. Effect of creep:
Detrimental results in RC structures due to creep:
a) Increased deflection of beams and slabs.
b) Increased deflection of slender columns (possibly leading to buckling)
c) Gradual transfer of load from concrete to reinforcing steel in compression members.
d) Loss of prestress in prestressed concrete.
6. In order to reduce the effect of creep-deflection it is advisable to use 0.2% of cross sectional area at the compression face.
7. Symmetrical arrangements of reinforcement will aid to avoid the differential restraint.
8. Reduction of moments on account of moment redistribution is generally NOT APPLIED TO COLUMNS.
9. Reinforcement availability:
Standard diameter sizes (mm): 6, 8, 10, 12, 16, 20, 24, 32, 40
Standard lengths: > 12mm diameter: 12 metres
< 12mm diameter: from a coil
10. These values are approximate and should be used only as a check on the total estimated quantity:
Slabs - 80 - 110 kg/m3 (flat slab120-220kg/m3)
Columns - 200 - 450 kg/m3
Walls - 40 - 100 kg/m3
R/C footings 70-90 kg/m3
Pile caps - 110 - 150 kg/m3
Rafts - 60 - 70 kg/m3
Beams - 150 - 220 kg/m3
Transfer slabs 150kg/m3
Retaining walls-110kg/m3
Stairs – 135kg/m3
Note: The actual reinforcement quantity in the element will vary according to detailing practice and efficiency of the concrete element.
11. In normal circumstances and where N grad concrete is used, forms may generally be removed after the expiry of the following periods:
Type of Form Work (Location) Min period before striking Form Work
a) Vertical formwork to columns, Walls, beam 16 - 24 hrs
b) Soffit formwork to slabs (props to be re-fixed immediately after removal of formwork) 3 days
c) Soffit formwork to beams (props to be re-fixed immediately after removal of formwork) 7 days
d) Props to slabs: (1) Spanning up to 4.5m 7 days (2) Spanning Over 4.5m 14 days
e) Props to beams & arches
12. CONCRETE MIX RULES OF THUMB
• ADDING 3L OF WATER TO ONE CUBIC METER OF FRESHLY MIXED CONCRETE WILL:
a. Increase slump about 25mm
b. Decrease compressive strength about 1 to 2 mPai
c. Increase shrinkage potential about 10%
d. Waste as much as 1/4 bag of cement
• IF FRESHLY MIXED CONCRETE TEMPERATURE INCREASES 10 DEGREES:
a. About 3L OF WATER TO ONE CUBIC METER maintains equal slump
b. Air content decreases about 1%
c. Compressive strength decreases about .5 to 1.2 mPai
• IF THE AIR CONTENT OF FRESHLY MIXED CONCRETE:
a. Increases 1%, then compressive strength decreases about 5%
b. Decreases 1%, then slump decreases about 10mm
c. Decreases 1%, then durability decreases about 10%
13. The main components of cast-in-place concrete floor systems are concrete, reinforcement (normal and/or post-tensioned), and formwork. The cost of the concrete, including placing and finishing, usually accounts for about 30% to 35% of the overall cost of the floor system.
14. Where normal 500 mPa reinforcement is utilized, a concrete mix with a compressive strength of 32mPa yields the least expensive system.
15. Where post-tensioned reinforcement is used, a concrete compressive strength of at least 40mPa psi is usually specified to attain, among other things, more cost-effective anchorages and higher resistance intension and shear.
16. Having the greatest influence on the overall cost of the floor system is the formwork, which is about 45% to 55% of the total cost.
Three basic principles govern formwork economy for site-cast concrete structures:
• Specify readily available standard form sizes. This is essential to achieve economical formwork. Most projects do not have the budget to accommodate custom forms, unless they are required in a quantity that allows mass production.
• Repeat sizes and shapes of the concrete members wherever possible. Repetition allows forms to be reused from bay to bay and from floor to floor, resulting in maximum overall savings.
• Strive for simple formwork. There are countless variables that must be evaluated and then integrated into the design of a building. Economy has traditionally meant a time-consuming search for ways to reduce the quantities of materials. For example, it may seem appropriate to vary the depth of beams with the loading and span variations, providing shallower beams where the loads or spans are smaller. This approach would result in moderate savings in materials, but would create additional costs in formwork, resulting in a substantially more expensive structure—quite the opposite effect of that intended. Providing a constant beam depth while varying the amounts of reinforcement along the span length is the simplest and most cost-effective solution.
17. ABRASIVE RESISTANCE of concrete increases with compressive strength and use of aggregate having low abrasion.
18. Do you know that:
For steel bars to lose one mm diameter due to corrosion, it takes about 12.5 years. But due to practical reasons the number of years reduces due to hostile corrosive environment. For 6mm dia To corrode completely it takes about 75 years.