Concrete Anchor Design in Top of Wall at Corner
kevin555582
6
I can't seem to find any details or other posts on this but could have missed them. For background: I am working on a concrete anchor design via ACI Chapter 17 in the top of a concrete wall, say 8" or 10", for tension only. This anchor is located at a corner. I am curious if the perpendicular wall can be used for breakout. It seems the value Anc could be adjusted to account for the perpendicular wall area. Or another way to look at it would be the value Anc could be reduced for the non-wall area. This seems similar to adjusting the area when anchors are close together. Curious what your thoughts are or how you handle this? Thanks.
In the past I've treated the condition in a similar way to the way you're describing when needed but I've only had to analyze it in this manner once or twice. I'm not sure on the specific condition that this is for but I would also recommended looking at the Simpson SB anchor to see if you're within range of their capacities. While it might not be an exact 1:1 comparison of your condition they could be useful for a general gut check depending on the conditions that you have