Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CFM to ft/min conversion 1

Status
Not open for further replies.

TheReg

Mechanical
Joined
May 20, 2003
Messages
14
Location
US
I need some help find a nice conversion from 680 CFM @ 5" static pressure to ft/min.
 
I'm going to assume the CFM is actual cubic feet per minute and not at standard conditions.

If the 680 cfm refers to standard conditions, you'll need to convert to actual conditions.

ACFM = 680 SCFM * (14.7/P1)*(T1 + 460)/520

ACFM is actual cubic feet per minute
SCFM is standard cubic feet per minute
P1 is flowing pressure, psia (psig + atmospheric pressure)
T1 is flowing temperature, deg F

If your flow rate is at standard conditions, you can neglect the 5" WC, its effect is neglible.

Once you know the actual flow rate and the duct size, it's simple to calculate the average velocity. All you need to do is divide the actual flow rate by the area of the pipe/duct it is in.

For example, 4" sch 40 pipe has an ID of 4.026 inches or an internal area of 0.0884 ft2. Therefore, the velocity is 7690 ft/min.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top