thread507-270275

I am doing an analysis on a building from the mid 1960's. I have a floor framing plan that references Ceco "14W4" or "14H4" bar joists. Span is 20ft. Can anybody tell me what the allowable uniform load might be or point me to a site that has a catalog for these joists?

KrisL
 
If these are 14H4 joists, a common nomenclature for open web joists, the 60 year Steel Joist Institute manual, for a 20 foot span, shows:

a maximum resisting moment of 212,000 in.#,
a maximum end reaction of 3500#,
a total load of 350 plf,
and an L/360 live load of 245 plf.

Hope this helps.

Mike McCann
MMC Engineering
 
Thanks for the quick response. The set of plans is very old and it looked like the "14H4" call-out might have been "14W4". Wasn't sure if this was some sort of proprietary nomenclature for Ceco joists.
 