Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CDEGs MALT and MALZ program

Status
Not open for further replies.

atlmat

Electrical
Joined
Oct 24, 2012
Messages
1
Location
US
We currently have CDEGS Multiground with MALT program, is MALZ program required for Substation Grounding Analysis?
 
It's been a long time but I remember using RESAP and MALZ when performing ground grid analyses.
 
MALT assumes that the potential at all points of the ground grid is the same. MALZ provides for voltage drops in the grid conductors. There can be a difference in large grids if the soil resistivity is low, but normally MALT is adequate for normal step- and toudh-voltage calculations. If there is a difference in grid potential, then the location of the fault is important, so it complicates the analysis.

MALZ also is needed to analyze high frequencies such as lightning.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top