Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

cast in situ concrete piles

Status
Not open for further replies.

sremotorway

Civil/Environmental
Joined
Sep 10, 2012
Messages
4
what is minimum time required to pour adjacent cast in in situ concrete piles with center to center distance of 3.2m.we are using reverse rotary method for boring of pile bores.
 
It likely depends on the soil type; in these environs it's not uncommon to have drilled piles @ 3x diameter drilled and concrete cast slightly later...

Dik
 
the subsurface strata is sandy from medium to dense.
 
If the holes are excavated immediately prior to concrete placement then a minimum strength of 80% of F'c is recommended before disturbing the adjacent soil. Using high early mix designs, this can be less than 24 hours.
 
sandy soil... any problems with sloughing of the sand? What is the reverse rotary method?

Dik
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top