This is a common issue and to get to the root of it would require many man hours. There have been numerous good points made that I completely agree with but I'll take a stab at clarifying a few things.
First, we need to incorporate some statistics here. Discussing a few points in space is difficult. If these samples were cast for ACI 318 code compliance, there should be two cylinders if cast in 6"x12" molds or three if cast in 4"x8" molds. Either way, a result is the average for that age (a single cylinder test is meaningless under the code, think of it as information only). You need to calculate the average (which is pretty much what everyone does), but you also need to look at the standard devaiation and the coefficient of variation for that test. Consult ACI 214 for assistance but this can be done readily in MS Excel or equivalent software by calling out the correct function. You need to understand how "good" the lab is at defining a result. If the coefficient of variation routinely runs over 4.0%, run away from that lab. A compotent CCRL accredited lab should be cranking out at below 2.0% with occasional instances between 2.0 to 4.0%. Now, once you start developing a history, that is more than 10 results on the same mixture, you can then determine the standard deviation for the population. At this point, you could then define the material variability by evaluating the population's standard deviation and laboratory's within-test standard deviation. ACI 214 spells out how to do this in detail so consult that document for assistance. ACI 214 is a required document for ACI's Concrete Laboratory Testing Technician - Grade II certification. All accredited labs should have at least one on staff (if not, ask why they don't as it is in their best interest). My point is that this individual should be able to assist.
If anyone is still reading this after the dismal science discussion, there is really no statistical difference between using an unbonded cap to a sulfur cap if the corresponding ASTM is being followed (C 617 vs. C 1231). You can easily screw up a sulfur cap just as bad as using an unbonded cap if you deviate from the documents. Sulfur caps require special gear and ventilation for protection while capping and attention to detail is a must as air voids, thick caps, and off axis capping can lead to garbage results. Unbonded caps must be rotated, as they will tear and degrade over time. Per ASTM C 1231, you can't use the pads past 100 uses. This is usually the biggest violation. All accredited labs must keep a record regarding the number of uses, make sure they are doing this. I personally recommend unbonded caps for concretes under 6,000 psi as it is far safer and friendlier to work with. Sulfur mortar is a solid at room temperature and must be heated to roughly 265 deg F in order to cast caps on to the concrete samples. The process is dangerous because your body is mostly water and it will boil that water in your skin if contact is made. It also generates sulfur gas which can cause skin irritation, nauseau, etc. Unbonded caps can be very successful if the testing protocols are followed; if not, garbage in equals garbage out.
One final note, a simple test on the labs part can be done. A compression machine is a simple device. A typical hydraulic machine has a base that is a ram and a top that holds the spherical head. The spherical head must be able to pivot to accept the 0.5% allowable off-axis sample (otherwise you would point load on one side). You should be able to walk up to this head, and be able to move the head with your hands around the spherical joint. If you can't, well...maintainence well need to be done, the head is not functional. Also, don't accept a load verification as compliance, there are many calibration points to consider besides "load". Surface planeness being one of the more important ones.
Good Luck.