amurray
Electrical
- May 5, 2005
- 34
We recently had an operation that caused 2 primary (2.4kV L-N) PT fuses to blow & are thinking it could be caused by Ferroresonace, but wanted to see if anyone has had similar experience.
A relay mis-operation (no fault) caused several CB to trip that left 2 cap banks (1200kVAR each) connected to a bus with no other source or load. Before the operation caps were online & bus was fed by utility & feeding load. I have attached a sketch to help illustrate the setup. Circuit breakers # 1 & #4 tripped.
Upon trying to re-energize the bus it was discovered that 2 primary PT fuses (1E) were blown (PT#2 on sketch). We know the PT were in-service prior to the mis-operation. Another set of PTs on adjacent bus did not blow fuse, but its fuses are 2E. Unfortunately we have no digital relaying for event records.
Anyone had similar occurrences?
Thanks
Andy
A relay mis-operation (no fault) caused several CB to trip that left 2 cap banks (1200kVAR each) connected to a bus with no other source or load. Before the operation caps were online & bus was fed by utility & feeding load. I have attached a sketch to help illustrate the setup. Circuit breakers # 1 & #4 tripped.
Upon trying to re-energize the bus it was discovered that 2 primary PT fuses (1E) were blown (PT#2 on sketch). We know the PT were in-service prior to the mis-operation. Another set of PTs on adjacent bus did not blow fuse, but its fuses are 2E. Unfortunately we have no digital relaying for event records.
Anyone had similar occurrences?
Thanks
Andy