can you cut into a 1" branch to add a sprinkler?

Status
Not open for further replies.

DBallz Sprinklerz

Mechanical
Joined
Apr 23, 2018
Messages
7
Location
US
Can you do it?

-defeated but not destroyed sprinkler designer
 
With the new 1" grooved stuff by victaulic I assume it would be easier. Regardless you can, but you have to cut out a section of pipe, put a nipple with 1" tee on one end and 1" union on the other end so the fitter can put it all back together.

How many sprinklers are going to be supplied from that 1" pipe now? You may have an issue with calcs at that point.

Travis Mack
MFP Design, LLC
"Follow" us at
 
Mechanically it is possible of course. Should you? That depends.
 