- Apr 7, 2008
- 1,176
We have a 2300hp 4.16kV motor that has recently been tripping out on high stator RTD values that are set to 135deg C per the motor datasheet. We seem to see these high stator temps when the motor is only running about 280A out of 312A full load. I have been trying to determine what could be causing this additioanl heating. Motor is in 40deg ambient temp and has a rated temp rise of 85deg C. This issue has just started happening recently.
We have consulted with the motor manufacturer and examined the motor thorughly for possible reasons that motor cooling may not be working. The motor is an open drip proof motor with baffels and rotor fins to circulate cooling air. Everything in motor seems to be o.k. including all rtd's and their connections. I should also note that there is a bout a 3% current imbalance on the motor when running however this imbalance has always been there.
This motor is connected to a 450kvar (2 250kvar caps in parallel)which is connected on the line side of the CT's in the protective relay which is providing current reading and therefore CT's are seeing total current of line and capacitor contribution. We have also verified CT ratios and they are correct. The caps in the pfc are connected in a delta configuration.
I wanted to know if it was possible that there could be an issue with the pfc that could be causing additional heating in the motor. If one of the caps in the pfc were to fail what would happen? Would we see unbalanced currents at the CT's downstream of the caps or would the line current for the lines connected to the failed caps just produce this extra reactive current for these phases thus not showing any changes on the downstream CT's?
I was going to hook a fluke power meter to the secondary of the CT's as well as PT's which are just upstream of the pfc. Will I be able to tell anything from this power meter. For instance will I see differnt power factors on the lines if one of the caps is bad? I would think not becuase as I mentioned the line current will just compensate for the extra vars showing no change on the downstream caps. Will there be any kind of voltage or current phase shift that can be seen?
A couple of other thought that pop into my head:
Can there be a possible harmonics issue that can cause this heating the we will be able to see?
Could these be a resonance situation between the cap and motor causing additional circulating current that we can see?
Thanks for the help.
We have consulted with the motor manufacturer and examined the motor thorughly for possible reasons that motor cooling may not be working. The motor is an open drip proof motor with baffels and rotor fins to circulate cooling air. Everything in motor seems to be o.k. including all rtd's and their connections. I should also note that there is a bout a 3% current imbalance on the motor when running however this imbalance has always been there.
This motor is connected to a 450kvar (2 250kvar caps in parallel)which is connected on the line side of the CT's in the protective relay which is providing current reading and therefore CT's are seeing total current of line and capacitor contribution. We have also verified CT ratios and they are correct. The caps in the pfc are connected in a delta configuration.
I wanted to know if it was possible that there could be an issue with the pfc that could be causing additional heating in the motor. If one of the caps in the pfc were to fail what would happen? Would we see unbalanced currents at the CT's downstream of the caps or would the line current for the lines connected to the failed caps just produce this extra reactive current for these phases thus not showing any changes on the downstream CT's?
I was going to hook a fluke power meter to the secondary of the CT's as well as PT's which are just upstream of the pfc. Will I be able to tell anything from this power meter. For instance will I see differnt power factors on the lines if one of the caps is bad? I would think not becuase as I mentioned the line current will just compensate for the extra vars showing no change on the downstream caps. Will there be any kind of voltage or current phase shift that can be seen?
A couple of other thought that pop into my head:
Can there be a possible harmonics issue that can cause this heating the we will be able to see?
Could these be a resonance situation between the cap and motor causing additional circulating current that we can see?
Thanks for the help.