Can anyone tell me what this European symbol on a oil filled xfmr temp monitor means? 1

Status
Not open for further replies.

bdn2004

Electrical
Jan 27, 2007
799
This symbol is on a xfmr vendor print. The gauge measures the temperature of the windings.
 
Replies continue below

Recommended for you

Windings are connected in parallel for the low voltage of a dual voltage transformer??

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
It's not a dual voltage transformer. And this symbol is not on the nameplate of the xfmr. It's a temp gauge on the transformer, and this device is part of it. It's wired out to terminals. RTD?
 
"Looks like" an RTD and a second RTD for the gauge?

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 

We were expecting an RTD that has three wires to monitor the winding temperature. That's what the PLC is set up to accept. There is a conflict between the PLC dwgs and the xfmr drawings. The PLC drawings show an I1+, I1-, and a ZP connection. I look through this article and see the 3-wire RTD shown..not exactly what we've got but close.
 
A WTI doesn't usually measure the winding temperature directly. They typically measure the oil temperature using a capillary bulb and use a CT hanging on one of the phases to drive a bias heater so that the winding temperature can be inferred from the oil temperature. The second element may be a trimming resistor for calibration.


 